BarFlyFisherman
NAXJA Forum User
PEOPLE DIE FROM INACCURATE INFORMATION.
Back-feed electrocution deaths:
http://www.electricenergyonline.com/?page=show_news&id=38786
http://www.cdc.gov/Niosh/face/In-house/full9005.html
http://incident-prevention.com/ip-a...rticle/115-hidden-traps-of-generator-use.html
C02 Poisoning:
http://www.cpsc.gov/cpscpub/prerel/prhtml04/04141.html
REAL REASON FOR SWITCHING (DISCONNECTING) THE NEUTRAL, has to deal with the "split" grounding conductors (dual grounding rods/neutrals) that are present when a portable generator is operating. [The following does not apply to a permanently installed stand-by generator (the neutrals & grounding conductors are continuous back to the service entrance (floating neutral connections in the transfer switch) AND the generator is grounded with it's own earth ground (at the generator).]
With a portable generator operational - the GFCI breaker protection on the portable generator will not operate correctly, as it will have TWO POSSIBLE neutral paths to return to ground (one at the service entrance & one at the generator). Since the generator's neutral must be bonded & grounded to earth, if the service entrance neutral is not disconnected, there will be TWO neutral paths & earth grounding points.
When a neutral is grounded in two places the voltage will split & the generator's breaker will trip. Then nothing will work.
WHY YOU DON'T WANT TO BACKFEED YOUR HOUSE SYSTEM BY PLUGGING THE PORTABLE GENERATOR INTO THE DRYER OUTLET:
The wiring inside of the wall from the panel to the dryer outlet may not be of sufficient size to handle the output from the portable generator. Overloading this wiring will cause it to overheat (like a toaster element) & posed a fire risk. If you thought you were cold before - imagine standing out in the storm watching your house burn down.
Backfeeding presents danger to utility workers and other homeowners.
Backfeeding your service panel through a dryer receptacle will feed power into the grid unless the main service breaker is opened first. Electricians working on the grid may be electrocuted when they encounter lines that they had assumed were safe (though they are taught to take precautions). You will also be supplying power to other homes on the same secondary distribution transformer that your home is on (aka:" islanding").
The utility company and your portable generator create phases that are not sync'd.
This means that if the utility power is restored while your portable generator is still backfeeding the power grid, your generator will be destroyed in a catastrophic manner. Your generator will burst into flames, igniting it's fuel tank & causing an even bigger fire (maybe your house?).
Reversed cord - energized prongs:
If the generator is on & the cord is unplugged from the dryer wall outlet, then there is a potential for electrocution. Those exposed prongs will have 240 volts!
Hazard at Generator
A lot of older houses do not have a dedicated grounding conductor at their receptacles. Many older homes used water pipes as the grounding rod. As water mains were replaced with plastic, the potential ground decreased. Additionally, few electricians ever test the resistance of the ground (using the fall of resistance method) to determine if a grounding rod is effectively discharging to earth (the resistance of the earth varies around the world). This incomplete discharge to earth results in the neutral conductor being energized, thus back-feeding the secondary side of the utility transformer. This is how a utility worker can be electrocuted.
Hazard at the Utility Transformer
If the utility company feed is not disconnected (main disconnect), your little portable generator will push power backwards to the utility company's step-down transformers. It will work in reverse, increasing this lower electrical voltage to thousands of volts. That will be more than enough juice to kill a lineman miles away!
While these would not occur if you threw your service disconnect - there are just too many "what ifs" and variables possible to guarantee that your system would operate safely.
THESE ARE ALL REASONS TO HAVE A QUALIFIED ELECTRICAL CONTRACTOR INSTALL A SERVICE DISCONNECT. It GUARANTEES that the lines are disconnected & reconnected in the correct order - eliminating the possibility of fire, injury, or death.
It is best to get one installed before you actually need it - during the summer months, when the electricians & parts are readily available.
Back-up generators are not just installed because there is a critical mission occurring inside the structure. Sometimes people want them just to stay comfortable during an outage, keep the wine cellar chilled, take a hot shower, read a book, heat the house, keep the freezer full of food frozen, etc. If you can afford to have and operate one - more power to you! (no pun intended)
P.S. My firm designs & installs permanently installed back-up generators (diesel, natural gas, and propane powered) at fine estate homes across the country. We also install underground diesel & propane tanks to power these generators. This is becoming a popular location as under ground they are not: visible (saving valuable real estate) or susceptible to damage from earthquakes, wildfires, vehicles, storms, etc.). I have a 30 kw natural gas powered (with a buried propane back-up tank). It will run on either fuel by merely the turn of a valve (that happens automatically when it senses a drop in natural gas pressure - like what occurs following a CA earthquake).
Back-feed electrocution deaths:
http://www.electricenergyonline.com/?page=show_news&id=38786
http://www.cdc.gov/Niosh/face/In-house/full9005.html
http://incident-prevention.com/ip-a...rticle/115-hidden-traps-of-generator-use.html
C02 Poisoning:
http://www.cpsc.gov/cpscpub/prerel/prhtml04/04141.html
REAL REASON FOR SWITCHING (DISCONNECTING) THE NEUTRAL, has to deal with the "split" grounding conductors (dual grounding rods/neutrals) that are present when a portable generator is operating. [The following does not apply to a permanently installed stand-by generator (the neutrals & grounding conductors are continuous back to the service entrance (floating neutral connections in the transfer switch) AND the generator is grounded with it's own earth ground (at the generator).]
With a portable generator operational - the GFCI breaker protection on the portable generator will not operate correctly, as it will have TWO POSSIBLE neutral paths to return to ground (one at the service entrance & one at the generator). Since the generator's neutral must be bonded & grounded to earth, if the service entrance neutral is not disconnected, there will be TWO neutral paths & earth grounding points.
When a neutral is grounded in two places the voltage will split & the generator's breaker will trip. Then nothing will work.
WHY YOU DON'T WANT TO BACKFEED YOUR HOUSE SYSTEM BY PLUGGING THE PORTABLE GENERATOR INTO THE DRYER OUTLET:
The wiring inside of the wall from the panel to the dryer outlet may not be of sufficient size to handle the output from the portable generator. Overloading this wiring will cause it to overheat (like a toaster element) & posed a fire risk. If you thought you were cold before - imagine standing out in the storm watching your house burn down.
Backfeeding presents danger to utility workers and other homeowners.
Backfeeding your service panel through a dryer receptacle will feed power into the grid unless the main service breaker is opened first. Electricians working on the grid may be electrocuted when they encounter lines that they had assumed were safe (though they are taught to take precautions). You will also be supplying power to other homes on the same secondary distribution transformer that your home is on (aka:" islanding").
The utility company and your portable generator create phases that are not sync'd.
This means that if the utility power is restored while your portable generator is still backfeeding the power grid, your generator will be destroyed in a catastrophic manner. Your generator will burst into flames, igniting it's fuel tank & causing an even bigger fire (maybe your house?).
Reversed cord - energized prongs:
If the generator is on & the cord is unplugged from the dryer wall outlet, then there is a potential for electrocution. Those exposed prongs will have 240 volts!
Hazard at Generator
A lot of older houses do not have a dedicated grounding conductor at their receptacles. Many older homes used water pipes as the grounding rod. As water mains were replaced with plastic, the potential ground decreased. Additionally, few electricians ever test the resistance of the ground (using the fall of resistance method) to determine if a grounding rod is effectively discharging to earth (the resistance of the earth varies around the world). This incomplete discharge to earth results in the neutral conductor being energized, thus back-feeding the secondary side of the utility transformer. This is how a utility worker can be electrocuted.
Hazard at the Utility Transformer
If the utility company feed is not disconnected (main disconnect), your little portable generator will push power backwards to the utility company's step-down transformers. It will work in reverse, increasing this lower electrical voltage to thousands of volts. That will be more than enough juice to kill a lineman miles away!
While these would not occur if you threw your service disconnect - there are just too many "what ifs" and variables possible to guarantee that your system would operate safely.
THESE ARE ALL REASONS TO HAVE A QUALIFIED ELECTRICAL CONTRACTOR INSTALL A SERVICE DISCONNECT. It GUARANTEES that the lines are disconnected & reconnected in the correct order - eliminating the possibility of fire, injury, or death.
It is best to get one installed before you actually need it - during the summer months, when the electricians & parts are readily available.
Back-up generators are not just installed because there is a critical mission occurring inside the structure. Sometimes people want them just to stay comfortable during an outage, keep the wine cellar chilled, take a hot shower, read a book, heat the house, keep the freezer full of food frozen, etc. If you can afford to have and operate one - more power to you! (no pun intended)
P.S. My firm designs & installs permanently installed back-up generators (diesel, natural gas, and propane powered) at fine estate homes across the country. We also install underground diesel & propane tanks to power these generators. This is becoming a popular location as under ground they are not: visible (saving valuable real estate) or susceptible to damage from earthquakes, wildfires, vehicles, storms, etc.). I have a 30 kw natural gas powered (with a buried propane back-up tank). It will run on either fuel by merely the turn of a valve (that happens automatically when it senses a drop in natural gas pressure - like what occurs following a CA earthquake).