ChuckstrPT said:
So,
We've got slightly less than 1000 sqft upstairs, and 2 ton unit that can't cool it down below 80 degrees when it hits 95degrees here (Alabama). Hotest room is our nursery, has the worst run of ducting. Have to nearly close off all the rest of the ducts to get any air in there. Plus attic access is in that closet, and does get hot. The system pretty much runs 24/7 during hot summer months.
So we have the system looked at....seems to be working fine, coolant checks out. Rec replace the whole system with a 2.5 ton unit for $5700. I asked about a 3 ton unit, was told Too Big. Funny, I didn't think you could ever have TOO MUCH AC? Apparently it's a humidity thing.
Does all that sound correct? and is that a fair price? We need resolution before July shows up again.
Thanks for any input!
Andy
I underlined a few clues to the problem.
Problem #1:
Is the attic/ceiling insulated? Wall insulation? (R-19 at ceiling and R-13 at walls -- minimum, more is better).
The old rule of thumb was 1-ton of cooling for every 400 square foot of
insulated conditioned space.
Rule of thumb: 1000 sq-ft => 2.5-tons (maybe a little short). Yes, a higher tonnage will condition an uninsulated space, for a greater utility cost (but only if you can move the greater airflow).
Problem #2:
No airflow to the nursery?
Is the air handler fan direct drive or belt driven? What is the duct pressure and airflow restriction compared to the blower rating?
Get the most airflow and pressure from your system.
Direct drive fan motors are typically multitap/multispeed motors, is yours on the high speed (high static pressure & airflow) motor wiring taps?
Belt driven fans are typically more robust that direct drive fans (more commercial grade). If you have a belt driven fan is it sheaved to run at enough speed and static pressure to overcome the long duct run restriction (the same question as the direct drive system)?
You need blower pressure and airflow capacity to get the refrigeration capacity delivered (and your system is not delivering the air, even if it's cooling fine).
Problem #3:
Is the duct to the nursery sized correctly?
What size (of the nursery & duct), what length duct, how many duct bends and twists?
The duct to the nursery is likely to be too small, and the register is also likely to be too small (your description of the air balance effort merits this diagnosis). Air is compressible and will not flow if the duct is too small or too restrictive (even with all other outlets closed, unless you increase the power by a cube factor).
Has anyone mentioned serving the nursery with larger ducting?
Problem #4:
Is return air ducted from the upper floor to remove the heat where it naturally travels (convection heat rises)?
If you donot have an upper floor returnair grille and duct, adding one will help extract the heat transferring through the walls and ceiling.
Pricing is specific to your area. $120/hr labor in San Franscisco will drive the cost there up more than the typical $45/hr in Littlerock. Equipment cost is similar nationwide but labor cost varies.
Get multiple estimates and ask questions. Ask them what the problem they see, and how they plan to fix it (besides isolating the solution to only a larger unit). If the current system cannot deliver airflow (develop sufficient pressure) to cool the nursery a unit change out is not expected to improve the performance unless it has high pressure features (commercial belt driven blower) or unless they reduce the duct restriction.
Insulate, match the system blower performance to the constructed duct restriction, reduce the duct destriction to better match (balance by design) the airflow restriction to each outlet, and extract (return) the hot air close to the source or where it collects.
Good Luck.