Apologies for the long post... but could use some help on this. Central air line into the house is freezing up again(81* inside). Guy that installed this thing gave me a "deal". I change the filter once a month or sooner like clockwork. I've read that it's either low on refrigerant or a plugged air filter (not the case). My blower is on right now but the unit is off to try and let this thing defrost. The more I read the bigger an idiot this guy seems to be. So a few questions:

Can or should I apply some heat to the line along with a hose out with the breaker off?

If there is a leak, shouldn't there be UV dye in the line so I can detect with light or glasses?

What can I do to get this to stop?
Thanks in advance.
 
A system that develops frost or ice on the evaporator or suction line can be caused by a number of things.

In no particular order:
Over charged.
Not enough heat available to boil off all of the liquid refrigerant in the coil.
Under charged
This takes a long time to ice up the coil.
Poor airflow
Dirty filter(s)
Dirty evap coil
Inadequate return air/poor duct design
Obstructed supply/return ducts
Improper indoor blower direction
Improper Installation
Too many possible issues to list


Need more info:
Make and Model # of the furnace, Evap Coil, & Condensing Unit
Square footage of the house
Pics of te installed system if you have any
 
Found the root issue, leak at one of the braised portions in the line. Refrigerant is low, very low, have a neighbor that knows how to do some of that. HVAC guy is evacuating the line fixing the leak, and recharging. It's a RUUD, 15 SEER, not sure of the model # being at work and all. Thanks for the help.

Just talked to the HVAC guy, he confirmed the leak with his sniffer. I was starting to think the SEER rating was too low, but he said it's ideal for my house.
 